General => General Forum => Topic started by: yankeeredneck on March 02, 2019, 10:19:02 AM
Title: Need lots of help lol.....
Post by: yankeeredneck on March 02, 2019, 10:19:02 AM
I am beating my head over this. As I have mentioned before in some of my posts, I am basically remodeling the family farm house. And boy am I running into some walls understanding a few things. Some history of the house......
House was built with 2x8 floor joists spaced 16 on center. The house is 30widex42long. The center girder is basically double 2x8 with a 2x8 on the bottom with posts every 10 feet. I know from basic structural engineering that it is not strong enough. Shoot....you can already tell that the floors are not even and the basic floor is like that of a bowl....sinking towards the center. My question is that if I add (4) 2x12 LVL together and put the posts at every 10ft, under the existing 2x8 structure, will it be strong enough. And basically do the same for right under the 14.5 ft of single 2x8 floor joists.
I have done a lot of searches and research but I am confused by the online calculators and stuff. I like things in plain English lol.
I will add pics in a moment to make sense of things.
Title: Re: Need lots of help lol.....
Post by: yankeeredneck on March 02, 2019, 10:31:47 AM
Here are the pics I have.....more to come with more of a pictorial of what I am looking to do
(https://imgur.com/iCjA1zO.jpg)
(https://imgur.com/TuKXxRD.jpg)
(https://imgur.com/UR1ph2i.jpg)
(https://i.imgur.com/SfCzMcI.jpg)
Post by: Nate R on March 02, 2019, 10:36:41 PM
We need more info. Is it a single story? 2 story? More? Snow loading?
Post by: yankeeredneck on March 03, 2019, 08:12:33 AM
Single story with a 5/12 roof on a not quite 8ft center block foundation. From what I see in code snow load is 20. The house is in Watauga county in western NC.  I am working getting more pics today. And the diagram of what I think I need to do but wanted other eyes looking just in case I missed something.
Post by: NathanS on March 03, 2019, 08:19:10 AM
Trying to keep the initial response simple,
You don't need calculators or LVLs (at least for now).
You need to spend a little time learning about the prescriptive tables in the code. They will give you max spans for joists (which yours are over span by a couple feet), and max spans for a girder (your double 2x8 beam).
Table R502.3.1 gives you living area spans for joists. By the book, you should have a girder midspan-ish under those joists.
Girder sizing is given in section 602. Provided that your girder is only supporting the floor, a double 2x8 can really only span around 5'. So you would either need posts every 4 or 5 feet, or simply frame a wall underneath it.
The worst part here is that you need a footing for either the posts or the wall to bear on.
There are tons of solutions to the problem, the question is what's the least back breaking. :)
If you want to jack the floor back up go very very slow, maybe over the course of weeks. I have never done anything like that, but if I was going through the effort of mixing concrete and pouring footings, and all that carpentry, I would jack that floor back up as close to level as I could get it.
Post by: NathanS on March 03, 2019, 08:24:49 AM
Code: https://up.codes/viewer/new_york/irc-2015/chapter/6/wall-construction#R602
WFCM: https://awc.org/pdf/codes-standards/publications/wfcm/AWC-WFCM2015-ViewOnly-1510.pdf
Post a diagram of the floor as you understand it. It is also important to know whether the roof is full span (outside wall to outside wall) or if some of the load is transferred down inside the building.
Post by: yankeeredneck on March 03, 2019, 08:32:08 AM
Thank you so much for the explanations!  That is what I was needing. I will get some plans down later this afternoon. I just want to make sure I am not over thinking the solution(s).
Post by: Nate R on March 03, 2019, 09:00:50 AM
Now you're getting there! I was going to go through the exercise of figuring out max loads on the girder and sizing it from there after adding up all the actual pounds of possible weight....But Nathan S's way is easier/better.
Post by: Don_P on March 03, 2019, 01:15:19 PM
Back out and take some general overview pics of the house to help give an idea of the building and foundation, you're in too tight for me to get oriented yet. I think I would use 30 psf snow in Watauga Co. If I'm understanding correctly the 2x8 floor joists are spanning about 15', that is also part of the deflection problem, they really shouldn't span more than about 12' so you are probably looking at a couple more girder lines under there to solve that problem. Back in the day it was very common for carpenters to use 2x8's for joists no matter what the span which leads to some pretty soft floors. Which way and how far from Boone are you?
Post by: yankeeredneck on March 03, 2019, 01:30:38 PM
You would be right on that. The single 2x8s are spanning around 14.5 to the double 2x8 center girder. What I am thinking is that about the 7ft mark on both sides of the center girder is to basically make 2 double 2x12 girder and put a 12inchx12inchx5ft sono-tube with  4 #4rebar in them every 10ft and a post on top of the sono-tubes. And I would then replace the center double 2x8 girder with the same double 2x12 set up as on the left and right side of that.
Please note that the flue will be coming out as they notched the girder to fit it in. I will be moving the wood stove to attach with the current HVAC system.
More images:
https://imgur.com/B2ewCaC
https://imgur.com/S3qsF7K
https://imgur.com/CbESlLE
https://imgur.com/BqJnamL
https://imgur.com/G6vXeLd
Drawing coming up soon
And Don....I am about 15 minutes outside of Boone....Valley Crucis  area
Post by: yankeeredneck on March 03, 2019, 02:04:19 PM
https://youtu.be/Ny3mlzFvb-Y
This might help some
Post by: yankeeredneck on March 03, 2019, 02:16:32 PM
Reason for all this is not only for the existing house but I plan on adding on a 16ft extension. Plus it just needs to be brought up to date some. This is my wife's family home and we both want it to last for the next generation and beyond.
Post by: NathanS on March 03, 2019, 02:24:14 PM
It's unnecessary to remove the doubled 2x8 girder. All you need to do is add more supports underneath it and it will be plenty strong enough.
Post by: yankeeredneck on March 03, 2019, 02:30:40 PM
An what about the 2x8 floor joists? Add a girder for them as well?
Post by: akwoodchuck on March 03, 2019, 03:49:29 PM
First, eat a good balanced breakfast....second, cut notches in block wall with a propane saw, run a couple steel I-beams through, jack up and shim in place....third, go eat lunch, you're done  :D
Post by: yankeeredneck on March 03, 2019, 04:01:24 PM
lol I actually have been debating that. The problem is.....what size I-beam if I go that route? Can I stay with a basic 10 or 12 inch I beam with 1/2 inch web or something different.
I guess that's the fun part of all this. I know either way I go.... it just needs to be done.
Post by: Don_P on March 03, 2019, 10:53:42 PM
If you can tolerate steel posts on 8' centers under the existing girder... Measure from slab to the underside of the girder and go get some steel posts at Lowes, or Parker Tie in W Jeff, not the telescoping ones but the type with a solid post and an adjustment screw. They come in various length ranges so just match up to your height range. Install those on 8' or closer centers.
You also need the 2 new runs of girders, they can be either 2 ply 2x8's with posts at 8' centers or 4 ply 2x8's with posts at 10' centers. This is going to be quicker and easier to adjust than the sonotubes and has plenty of strength for the application, I've just done something similar in an underbuilt commercial building.
If the slab is not capable of supporting 2800 lbs per post @8' or 3500 lbs @10' then you need to spread the footprint over a larger area. I poured 18" square x 8" thick pads on top of the slab and put the posts on those, I had significantly higher loads. I suspect 8x8x1/2" steel plate between the slab and post would be plenty here to distribute the load. I ran the numbers using #2 southern yellow pine which it appears you have and is readily available. Anyway, install, snug them up and then slowly apply pressure till you get to the happiest place you can. I ended up lifting the center girder off those posts slightly in an attempt to get the floor's deflection set to flatten some on our project.
I'd be willing to bet the chimney does not notch into the girder, simply into that worthless plate under the girder. There was a thinking problem going on there. They were using that plate to "support" the joists framing into the girder rather than joist hangers. If that is the case it wouldn't hurt to check to see that none of the joists have slid downward, look at the top of the girder and the top of the joist up against the subfloor at each location. If the nailing was good and it is in plane don't worry about it, you are picking up more support here. If things have drifted then it needs to be addressed. Anyway that is all a quick and simple fix.
We were married in Valle Crucis, the old St Johns Church. I'm about 70-80 miles north but can see Grandfather from the peaks here on a clear day. I heard they clocked 124 mph for 3 seconds there last week.
Post by: yankeeredneck on March 04, 2019, 07:11:21 AM
Don,
Thank you for the solution you have presented. I just might do it since I was leaning toward that way but with 2x10 or 2x12 doubled up. The girder has drifted just a little....like by a half inch. My plan was to add a steel I-beam under the existing girder and create basically the same thing on the mid way points of both sides to make sure I am even all the way.
Yes, Grandfather MTN did set a record that day of just slightly over 124mph. I am about 20 -30 minutes from there on the Foscoe side of Valley Crucis. And yes, I know the church you guys were married in. Nice to know I have someone close by me
I will update when I can on the progress of this project. Many more to come lol
And thank you all for the responses. I have learned a lot from everyone here.
Post by: Don_P on March 05, 2019, 09:59:08 PM
Ah, back up, I made an assumption I shouldn't have. Is there a load bearing wall above that girder running the length of the house that in turn supports part of the roof?
Post by: yankeeredneck on March 06, 2019, 07:04:54 AM
There seems to be. I have been up in the attic area and it looks like it.
Am I going back to the 2x12 scenario?lol
Post by: Don_P on March 06, 2019, 07:41:02 AM
Go back up into the attic. Are there ceiling joists lapped over that center wall? If so the girder is picking up an additional ~10 psf. Next are there vertical or canted posts or studs holding up the rafters or ridge from over that center wall? If so the girder is also supporting roof weight ~30-40 psf.
Post by: yankeeredneck on March 06, 2019, 07:47:24 AM
I can tell you that yes, the roof is connecting to the center wall. And yes, there are vertical 2x8s as well on the center wall. The 2x8s run vertical and angled every 16 on center I believe.
Post by: Don_P on March 06, 2019, 10:30:34 PM
Well that's not good for the basement problem.  I'd say you ought to count on at least 16' of the roof width bearing on the girder x 10' post spacing x 40 psf= 6400 lbs plus the 3500 pound floor load, we're at 10,000 lbs per 10' span, and I would reuse the post locations, there should be a footing under the slab there, you can drill to confirm that but they have worked in those locations thus far. So the center girder needs something more substantial. You also need a way of getting it in, door or window in that axis with it or remove a few blocks, you'll probably be bringing it in in 20' pieces. I believe a W8x13 should do it in an I beam, that is 8" deep and 13 lbs per foot. A W8x10 barely works, I think I'd go a little heavier. In LVL a triple 9-1/4" deep would work. The supplier can check the engineering on that, I think that would be the easier solution and can come with an engineers stamp.
For that raising script, you are installing the new girders and taking some of the load, bring in the lvl's and set them on the floor beside the existing posts. Then build shoring on each side of the existing girder to take the load off the existing posts, drop the old posts, raise the new girder under the old and replace the posts. I'll try to get some pics of one way to do the lateral bracing of all of the new dropped girders, they need to be laterally braced to prevent rolling over each post.
Post by: yankeeredneck on March 07, 2019, 07:00:30 AM
I figured I would have to replace the center girder. Gut feeling.
And I appreciate the help on this Don. And again thanks to everyone here on the forum. You guys are some of the best out there!
Post by: Don_P on March 07, 2019, 09:22:09 PM
That does bring up another way. If you can tolerate a wall under the existing girder that would also work, another way of thinking about the old saying "many hands make light work". A treated plate bolted to the slab, run a stringline 1-1/2" below the girder as a straight reference and cut studs that measure from top of plate to string + 1-1/2" and knock them in to vertical would flatten and support the girder. Header any openings and then sheath the wall to prevent the studs from bowing. Just one more option.
Post by: yankeeredneck on March 08, 2019, 06:58:44 AM
I have thought about that. I would think that a 2x8 16 on center and leave an area to go to either side (maybe with a door or 2) would be sufficient. Still would have to do something on either side of the center girder but a double 2x8 like the center girder should be enough to hold up 7 1/2ft of single 2x8 floor joists. And have a post every 10ft.
MAny option.....all depends on what the wife wants to do. I will update as I can on this as you guys have given me many thoughts on this.
Post by: yankeeredneck on March 08, 2019, 12:42:27 PM
I think I have been shocked ....lol Wife approved the wall set up. She liked the idea of sectioning the basement so she can have an area for canning and I can have a place for my computer servers ( I work in IT ). About blew me away lol.
I'm thinking about doing a 2x8 wall 16 on center and a structure block in between them with a opening right in from of the stairs....its only about a 3ft section. And then do the double 2x12s for the left and right girders with a post at the 10ft mark on each of those. Sounds like I have a plan in place.
Post by: yankeeredneck on March 12, 2019, 05:49:32 PM
Here is what I am planning:
(https://imgur.com/FZEOxQP)
Where there are the two areas that look like they open up to each side would be correct. Where the stairs are, I do plan on doing a wall as well. Those are 4x4 posts set every 2 feet. I know I am over thinking and over doing the structuring, but I think it should work.
What do you guys think
Post by: Don_P on March 12, 2019, 09:24:41 PM
Under the center girder, building a wall with a treated 2x4 bottom plate, running 2x4 studs on 16" centers and sheathing the wall preferably with 1/2" osb or ply would be quite sufficient and would make a better wall than 4x4's on 2' centers. For your other posts, a 4x4x8' is good for around 4000 lbs, a 6x6x8' is good for around 14,000 lbs, however, the steel BOCA posts have an adjustable screw jack and are plenty strong enough for these loads. I believe any of these are going to be stronger than your nail laminated columns and probably cheaper. I'm not understanding where the I beam figures in but if it is an attempt at stiffening the joists it probably won't have sufficient shear connection to do much there.
Post by: yankeeredneck on March 13, 2019, 06:13:59 AM
Don
I see where you are going with the design. Basically your standard 2x4 wall with 16 on center (PT of course for anything touching the concrete) will be better. And the 4x4 posts will be just for holding up the stairs. So a standard 2x4 wall and at the openings for each pass through just make sure I do the correct header is what you are saying?
The BOCA posts will be what I would be using for the left and right girders any way.
Post by: Don_P on March 13, 2019, 06:24:00 AM
There ya go. One problem I've seen, and felt, is the framers will build a 2x4 load bearing wall in the basement and then it doesn't get sheathed. Then under load the 2x's bend sideways under load. It doesn't really take much to hold them in line to kill that bowing and vibration, then as a stiff wall it is more than adequate.
Post by: yankeeredneck on March 16, 2019, 07:33:31 AM
Well, hopefully today I do the wall with my brother-n-law and nephew. Hopefully pics to come of the work in progress and completed.
Post by: yankeeredneck on March 17, 2019, 03:01:21 PM
Had a small set back but should have things done this week. I do have one other question.
Do I still have to have the left and right girders done? I figured a double 2x12 with the posts every 10ft but wanted to make sure if the center girder wall will basically carry the structure correctly.
Post by: akwoodchuck on March 17, 2019, 03:40:40 PM
I'd say you do need those beams....you're way over what I would consider acceptable span for rough cut 2x8s and diagonal sheathing....but I really hate bouncy floors...
Post by: yankeeredneck on March 17, 2019, 05:02:49 PM
Quote from: akwoodchuck on March 17, 2019, 03:40:40 PM
I hate bouncy floors as well. My plan is to cut in the double 2x12s and add hangers for the 2x8 to the double 2x12s. And of course the posts every 10 ft.
Post by: Don_P on March 17, 2019, 06:48:53 PM
Hmm, lets do some math. You would be supporting about 7' of width... halfway towards the exterior wall and halfway towards the center girder x 10' between posts x (40+10psf)= 3500lbs
http://www.timbertoolbox.com/Calcs/ddsimplebeam.html
Back out and put in these inputs;
3500 lbs
120" span
4.5 wide
7.25" deep
#1 SYP 8" wide
10 year
3 members
2x8
No
No
That is one way, you need to break over each post. If you can drop to 8' post spacing then 16' lumber can be "woven" over the posts making for a stronger better beam and 2 @2x8 should work. You can playe with other depths and combinations, point being it probably doesn't have to be 12" deep, nothing wrong with that just more options available. Cutting the gap is not fun!
One more, double up the existing joists, no additional girders, deflection barely fails but is improved by 50%. Tipping up joists, especially in a deflected floor is not fun either. This is the least stiff option but avoids additional girders and posts.
Post by: yankeeredneck on March 18, 2019, 06:12:33 AM
Quote from: Don_P on March 17, 2019, 06:48:53 PM
About that Don
I wondering about that. It had been suggested that I add a 2x12 to the current 2x8 and I should be able to not have the additional girders. What's your opinion on it?
Post by: Don_P on March 18, 2019, 07:54:29 AM
2x10's would be plenty but you do run into an issue at the ends. They need to notch back down to 2x8 at the bearings. Although a 1/4 depth square notch is permissible that causes a stress concentration at the re-entrant corner, the inside corner, of the notch. In plain speaking it tends to cause a split to form from the notch. Can't tell you how many times I've seen that in old work. It is better to drop down from the notch at a shallower angle or an arc than to have a sharp cornered notch.  If you build some forked long levers out of 2x lumber bolted or heavily screwed together it helps when tipping up the new joists. I have both sistered alongside the existing joists and also simply run centered between the existing and blocked the new ones in there rigidly. I think sistering with plenty of nails is probably better but can be a real pain to get them up tight without breaking the new joists. A bottle jack on its side with pump down can help but takes several hands, and watch what you are doing to the joist you are pushing against. It is all patient work, if frustration rises its time to go split some firewood  :D.
Post by: yankeeredneck on March 18, 2019, 04:39:26 PM
Quote from: Don_P on March 18, 2019, 07:54:29 AM
Any way you can show me what your talking about here? I think I understand it but want to make sure what I am thinking is what you are describing.  (lol) Would I still need the left and right girders if I did it this way?
And yes....busting wood the old fashion way is a nice way of relieving stress lol
Post by: Don_P on March 18, 2019, 09:17:28 PM
You would not need the additional girders doing it this way. The floor is now actually strong enough with the reinforced center girder, it lacks stiffness which is a serviceability issue rather than a strength problem. So what you are now doing is stiffening the floor until you find it acceptable. I would start by doing every other joist, see how it feels and then deciding whether to do every joist.
Here is what we call the tweaker, pretty simple, make it out of scrap, the handle is about 6' long, make 2 and have a man towards each end twisting the joist upright. Inspect the floor above you for protruding nails etc. Typically put the top of the joist as near as possible to where you want it and twist the bottom under it.
(http://timbertoolbox.com/cp/tweaker.jpg)
Post by: yankeeredneck on March 19, 2019, 06:06:09 AM
Don
So you are saying put one of these under the ends of the joist after adding the sister joist?
Note: Never mind---- did a quick Google search and answered my own question on that
Post by: Don_P on March 19, 2019, 06:59:40 AM
Now I'm not sure what google told you  :D
That is simply a tool to give you leverage to twist the joists into place, it will not remain in the finished project in any way.
Let's back up and explain the options here. Since this is a performance enhancement there are several levels of performance you can get to. The stiffest floor would be to install the additional rows of girders. If you prefer a very solid floor or intend to install tile at some point, that would be the way to go. At the least stiff end of that spectrum would be to double up the joists with 2x8's. Deeper joists are considerably stiffer than shallow ones, so each time you step up to a deeper joist the stiffness improves. Because of your 2x8 end bearing depth I suggested a compromise of using 2x10's. This stays within the notching rules which are about horizontal shear, the splitting I mentioned above, and gives what I believe will be sufficient stiffness to be satisfactory but it will not be concrete stiff. Hope that clarifies your options better.
Post by: yankeeredneck on March 19, 2019, 04:53:50 PM
Don
Yes it does and yes the tweaker is what I thought it was. Although I will be doing the joist sistering later on....like in a month or two... my plan is to stiffen the floors up. By doing the 2x12 route with the notched end not only round at the "corner" but I also planned on 2x4 wall under the ends against the concrete walls of the basement. And sense I had planned on sheathing the center girder wall anyway.... I will notch the 2x12 to fit the wall and new wall and use hangers there. and stagger 2x8s in between the joists to make the joists connect. I know this might be over kill but not worried about that. I just want it so that way when my kids jump....it does shake the whole house lol
Post by: NathanS on March 19, 2019, 07:54:58 PM
Yankee, just curious... you're thinking about adding joists because you don't want the additional posts in the basement?
I am just reiterating what has been said... you will have a better floor if you add the girders and leave the joists alone.
Adding those joists is going to be back breaking, knuckle busting, lots of cursing pain. From the pics it looks like you may have to move wiring too... hopefully no plumbing or duct work is in the way.
Post by: yankeeredneck on March 20, 2019, 06:13:03 AM
NathanS
That would be correct. I really don't "want" to add them but if I must, I must. As for the wiring and plumbing....that's all getting redone so it won't matter to me on that. I still have cast piping in the house for the septic. And cloth wrapped 60's wiring in the house for a good chunk of the house. The HVAC just got put in.
If I must add the left and right girders....then so be it. A double 2x10 with a post every 10ft passes the tests per the timbertoolbox site.
Post by: yankeeredneck on March 23, 2019, 07:24:55 PM
Wall has been started. Should be finished tomorrow. Pics to come .... stay tuned
Post by: yankeeredneck on March 24, 2019, 04:55:07 PM
https://imgur.com/guv5mld
https://imgur.com/bnPXLRh
https://imgur.com/9RG5SBj
https://imgur.com/7EuTNtu
https://imgur.com/R2Be5id
https://imgur.com/5np65Ew
https://imgur.com/P4gBsFN
https://imgur.com/L0egShU
https://imgur.com/kojUKjf
https://imgur.com/m7hWeYC
https://imgur.com/c98CIB9
https://imgur.com/qJA9bx4
Have the wall done except for the sheathing. There was only a few dollars difference between 1/2 inch OSB and 3/4 T&G Flooring OSB.....so I went with the  3/4 inch. Sheathing will go on later this week.
Don....Thank you for all your help in this. You too NathanS. Everyone here on the forum.... excellent advise and knowledge.
Post by: yankeeredneck on March 28, 2019, 07:15:51 PM
Finished Project:
https://imgur.com/lZbQJDk
https://imgur.com/gisBW9N
https://imgur.com/rHgpN7d
Post by: Don_P on March 28, 2019, 08:42:33 PM
Looks good, did it improve the flatness? How does the floor feel at this point?
Post by: yankeeredneck on March 29, 2019, 06:21:55 AM
It did improve the flatness. After doing a lot of measuring, the floor whole length of the girder went like this : ^   ^   ^   ^  ^ at every 8ft; which is where the posts were. So we basically left those peak areas loose in the wall and it has actually settled back down just about perfect. Now everything is within 1/8 of an inch or closer. Not bad!
The stiffness is much better. It still shakes the house when the kids jump but is not as bad. Once I get the left and right girders done and add some blocking in between; I'd say that will stiffen the floor right up.
When I do those I will make a new post. Right now  I have to concentrate on the farm. Hopefully in a month or so I can get back onto the house.