Engineering - For beginners, Part 3

Started by RAB, January 07, 2005, 11:55:11 PM

Previous topic - Next topic

0 Members and 2 Guests are viewing this topic.

RAB

Key Elements for Deflection Ratios

Common minimum ratios for deflection in residential construction.
 
These are the minimum deflection values from the most widely used residential codes; most designer/engineer/builders have used these for base values with out much change for a number of years.
 
Rafters having no finished ceiling      1/180
Interior walls with non-brittle finish  1/180
Interior walls with brittle finish         1/240
Exterior walls with non-brittle finish  1/360
Floors and finished ceilings                1/360
Exterior walls with brittle finish          1/361 (not a typo)

1/360 = 1" of deflection in 360" or ½" of deflection in 180"

  **General Rule about Deflection Ratio**
As the finish becomes more brittle and the application is more noticeable a higher deflection ratio is needed.

Example based on finish: Sheet rock compound and plaster should have a support structure higher than 1/239.
Example based on application (structural movement): Wall assemblies around doors and windows should not deflect more than 1/360 or 3/16" in 76".
Example based on application (perceived vibration): Floor joists should not deflect more than ½" per 180" (1/360) of span

  **Ryan's Rule of Floor Deflection**
1/360 minimum ratio should be used in closets and spare bedrooms. Deflection ratios around 1/480 have best cost –to- deflection perception value.

  **Ryan's Rule of Door and Window Header Deflection**
1/8" maximum total deflection regardless of size.

Interested readers – this is a multipart series
Engineers please excuse the simplification that this forum dictates.

Ryan B